When must a neutral conductor be counted as a current-carrying conductor for ampacity adjustment under NEC 310.15(E)?
Correct Answer:
When it carries only the unbalanced current from other conductors of the same circuit, it is not counted; it is counted when it carries a portion of the nonlinear load current, as in a 3-phase, 4-wire, wye-connected system with nonlinear loads