Ungrounded conductors of a 20-ampere circuit are increased from 12 AWG copper to 8 AWG copper because of voltage drop. The overcurrent device remains 20 amperes. Under 2020 NEC 250.122(B), what equipment grounding conductor action should the inspector require?
Correct Answer:
Increase the copper equipment grounding conductor proportionately from 12 AWG to 8 AWG, unless a qualified person sizes it to provide an effective ground-fault current path under the 250.122(B) Exception