Transformer secondary conductors are not considered protected by the primary overcurrent device unless they comply with NEC 240.21(C). For the 10-foot secondary conductor rule in 240.21(C)(2), which condition must the inspector verify?
Correct Answer:
The secondary conductors have an ampacity not less than the secondary current rating of the transformer, and the length is not more than 10 feet, with termination in a single overcurrent device