After oil piping is installed and before it is concealed, NFPA 31 8.8.1 requires which tightness test?
Correct Answer:
A hydrostatic or pneumatic test at not less than 1-1/2 times maximum working pressure, but not less than 5 psig, held at least 30 minutes.