A TXV-equipped R-410A unit has a liquid-line pressure that corresponds to 110°F saturated condensing temperature. The measured liquid-line temperature at the condensing-unit outlet is 98°F. Manufacturer target subcooling is 10°F. The system subcooling and most likely charge condition are:
Correct Answer:
12°F subcooling; slightly overcharged