A service disconnect is installed outside a commercial building, and the metering equipment is on the same exterior wall. Under NMAC 14.10.4.12 (amending NEC 230.70), where must the inspector require that outdoor service disconnect to be located?
Correct Answer:
In a readily accessible location within 48 inches of the metering equipment; a remote disconnect not more than 10 feet from the building is considered to be located on the building