A plan lists only appliance input ratings in Btu/h. Before entering a UMC natural-gas sizing table that is printed in cubic feet per hour, what conversion should the inspector require?
Correct Answer:
Divide each input by the local heating value in Btu per cubic foot (commonly about 1,000 Btu/cf) to obtain CFH

Access more questions from this quiz