A non-voice fire-alarm panel draws 0.25 A in standby and 2.00 A in alarm. Using NFPA 72-2010 durations (24 h standby + 5 min alarm) and a 20 percent safety factor, what is the minimum battery capacity?
Correct Answer:
7.4 AH