A floor-mounted gas furnace with a listed flammable-vapor-ignition-resistant (FVIR) rating is installed in a residential garage with its ignition source 6 inches above the floor. How should a New Mexico CID mechanical inspector treat the installation under 14.9.2.11 NMAC?
Correct Answer:
Reject it; New Mexico deletes the UMC text “unless listed as a flammable vapor ignition resistant,” so the ignition source must still be elevated