A building heat loss is 48,000 Btu/h at an outdoor design of 20°F with 70°F indoors (50°F difference). The heat pump's heating capacity at 20°F is 36,000 Btu/h. Which statement is correct?
Correct Answer:
20°F is below the balance point, so supplemental heat is required to meet the 12,000 Btu/h shortfall