A 69 kV effectively grounded wye transmission line crosses a public road. NESC 2007 Rule 232B1 requires Table 232-1 clearances to be increased 0.4 inch for each kilovolt over 22 kV to ground. Using Vlg = 69 / 1.732 = 39.8 kV, what is the approximate required roadway clearance for open supply conductors?
Correct Answer:
19.1 feet