A 500 kVA three-phase transformer is rated 12,470 V on the primary. Using NEC Table 450.3(A) for an unsupervised location, the maximum primary circuit-breaker setting is 300 percent of rated primary current. What is the next standard breaker size permitted by Note 1 if the calculated maximum is not a standard rating?
Correct Answer: