A 480Y/277-volt, 75 kVA dry-type transformer in an Anderson mechanical room is a separately derived system. The secondary ungrounded conductors are 3/0 AWG copper. What table is used to size the system bonding jumper?
Correct Answer:
Table 250.102(C)(1) or Table 250.66, based on the derived ungrounded conductors

Access more questions from this quiz