A 140,000 Btu/h atmospheric gas boiler is installed in a 30 ft × 20 ft × 8 ft room with no outdoor combustion-air openings. Using the indoor standard method, is the volume adequate?
Correct Answer:
No. Required volume is 7,000 ft³ and the room has only 4,800 ft³.