A low-pressure steam boiler must serve 800 square feet of steam EDR. Using 240 Btu/h per square foot EDR and 33,475 Btu/h per boiler horsepower, what net output and approximate boiler horsepower are required before pickup?
Correct Answer:
192,000 Btu/h; about 5.7 BHP