Why may a contractor start an ampacity adjustment calculation in the 90°C column for THHN, even when the circuit breaker is marked 75°C?
Correct Answer:
Because 310.15(A) and 110.14(C) allow the 90°C ampacity to be used for adjustment and correction, provided the final ampacity does not exceed the 75°C termination rating

Access more questions from this quiz