A 4,000 cfm indoor-return air handler has no smoke detector for automatic shutoff. The contractor points to the evaporative-cooler exception in 14.9.2.14 NMAC. What should the inspector do?
Correct Answer:
Reject the argument; the evaporative-cooler exception applies only to coolers that derive all of their air from outside, not to indoor-return air handlers under UMC 609.1

Access more questions from this quiz