An underground polyethylene fuel-gas service is installed without a tracer wire. How should the inspector treat the installation under UMC Chapter 13?
Correct Answer:
Reject it; nonmetallic underground gas piping must be installed with a means of locating the pipe, typically an insulated copper tracer wire, as required by the fuel-gas piping chapter