A second building on a property is supplied by a 120/240-volt feeder that includes an equipment grounding conductor. Under NEC 250.32(B), how must the inspector require the grounded conductor and equipment grounding conductor to be treated at the second building?
Correct Answer:
The equipment grounding conductor must be connected to the building disconnect enclosure and to the local grounding electrode system, and the grounded conductor must not be connected to the enclosure or electrode system, except as permitted for existing installations