A manufacturer’s instruction for a natural-gas furnace installed at 5,000 feet says to reduce nameplate input 4 percent for each 1,000 feet above 2,000 feet. The nameplate is 100,000 Btu/h. What input should you set and use for combustion-air and gas-pipe load?
Correct Answer:
88,000 Btu/h (12 percent derate: 3 × 4 percent)