An isometric of a public toilet room shows eight floor-outlet water closets on one horizontal branch with a single vent rising between the two most upstream trap arms. Under UPC 2021 Section 911, that vent is a circuit vent and shall be not less than:
Correct Answer:
2 inches, and increased per Table 703.2 if the circuit-vented DFU load requires it