An HVAC technician is troubleshooting an R-410A commercial split system. The liquid line gauge pressure reads 318 psig (corresponding to a saturated condensing temperature of 100°F), and the measured liquid line temperature at the outlet of the condenser coil is 88°F. What is the system subcooling, and what does this indicate if the manufacturer design subcooling is 12°F?
Correct Answer:
Subcooling is 12°F; the system subcooling matches manufacturer specification exactly.